  • in reply to: running television off leisure batteries. #138485
    Ste_Mulv
    Participant

    Hi All,
    Just these posts and

    Hi All,

    Just these posts and there are two things:

    If the voltage sensitive relay has no instructions, contact the manufacturer as if you get the system wired the wrong way round, you could end up emptying your leisure battery into you main battery or it not working at all. They will be able to help in no time and accurately.

    The other point is on the invertor, you can easily electrocute yourself when you are playing with 230VAC and it is deadly. Ensure you fuse the 12v to the invertor and Residual current device (RCD) protect the output of the invertor (ensure you check your earthing system too). Don’t forget that an RCD is there to save your life, I always choose quality products in this type of situation.

    Regards,

    Steve

    in reply to: running television off leisure batteries. #138490
    Ste_Mulv
    Participant

    Hi All,
    Just these posts and

    Hi All,

    Just these posts and there are two things:

    If the voltage sensitive relay has no instructions, contact the manufacturer as if you get the system wired the wrong way round, you could end up emptying your leisure battery into you main battery or it not working at all. They will be able to help in no time and accurately.

    The other point is on the invertor, you can easily electrocute yourself when you are playing with 230VAC and it is deadly. Ensure you fuse the 12v to the invertor and Residual current device (RCD) protect the output of the invertor (ensure you check your earthing system too). Don’t forget that an RCD is there to save your life, I always choose quality products in this type of situation.

    Regards,

    Steve

    in reply to: running television off leisure batteries. #138492
    Ste_Mulv
    Participant

    Hi All,
    Just these posts and

    Hi All,

    Just these posts and there are two things:

    If the voltage sensitive relay has no instructions, contact the manufacturer as if you get the system wired the wrong way round, you could end up emptying your leisure battery into you main battery or it not working at all. They will be able to help in no time and accurately.

    The other point is on the invertor, you can easily electrocute yourself when you are playing with 230VAC and it is deadly. Ensure you fuse the 12v to the invertor and Residual current device (RCD) protect the output of the invertor (ensure you check your earthing system too). Don’t forget that an RCD is there to save your life, I always choose quality products in this type of situation.

    Regards,

    Steve

    in reply to: running television off leisure batteries. #138493
    Ste_Mulv
    Participant

    Hi All,
    Just these posts and

    Hi All,

    Just these posts and there are two things:

    If the voltage sensitive relay has no instructions, contact the manufacturer as if you get the system wired the wrong way round, you could end up emptying your leisure battery into you main battery or it not working at all. They will be able to help in no time and accurately.

    The other point is on the invertor, you can easily electrocute yourself when you are playing with 230VAC and it is deadly. Ensure you fuse the 12v to the invertor and Residual current device (RCD) protect the output of the invertor (ensure you check your earthing system too). Don’t forget that an RCD is there to save your life, I always choose quality products in this type of situation.

    Regards,

    Steve

    in reply to: running television off leisure batteries. #138489
    Ste_Mulv
    Participant

    Hi All,
    Just these posts and

    Hi All,

    Just these posts and there are two things:

    If the voltage sensitive relay has no instructions, contact the manufacturer as if you get the system wired the wrong way round, you could end up emptying your leisure battery into you main battery or it not working at all. They will be able to help in no time and accurately.

    The other point is on the invertor, you can easily electrocute yourself when you are playing with 230VAC and it is deadly. Ensure you fuse the 12v to the invertor and Residual current device (RCD) protect the output of the invertor (ensure you check your earthing system too). Don’t forget that an RCD is there to save your life, I always choose quality products in this type of situation.

    Regards,

    Steve

    in reply to: running television off leisure batteries. #138502
    Ste_Mulv
    Participant

    Hi All,
    Just these posts and

    Hi All,

    Just these posts and there are two things:

    If the voltage sensitive relay has no instructions, contact the manufacturer as if you get the system wired the wrong way round, you could end up emptying your leisure battery into you main battery or it not working at all. They will be able to help in no time and accurately.

    The other point is on the invertor, you can easily electrocute yourself when you are playing with 230VAC and it is deadly. Ensure you fuse the 12v to the invertor and Residual current device (RCD) protect the output of the invertor (ensure you check your earthing system too). Don’t forget that an RCD is there to save your life, I always choose quality products in this type of situation.

    Regards,

    Steve

    in reply to: running television off leisure batteries. #138501
    Ste_Mulv
    Participant

    Hi All,
    Just these posts and

    Hi All,

    Just these posts and there are two things:

    If the voltage sensitive relay has no instructions, contact the manufacturer as if you get the system wired the wrong way round, you could end up emptying your leisure battery into you main battery or it not working at all. They will be able to help in no time and accurately.

    The other point is on the invertor, you can easily electrocute yourself when you are playing with 230VAC and it is deadly. Ensure you fuse the 12v to the invertor and Residual current device (RCD) protect the output of the invertor (ensure you check your earthing system too). Don’t forget that an RCD is there to save your life, I always choose quality products in this type of situation.

    Regards,

    Steve

    in reply to: Solar Panel Help #137217
    Ste_Mulv
    Participant

    REPLY Solar Panel Help
    Hi Chris,

    I just searched in google for “12v Solar Panel Regulators” and I quickly found this product which would more than suit your need and it also has isolated dual outputs so you can connected to you main and leisure batteries to keep them both topped up with out worrying about draining you main battery. I have a fairly good knowledge of solar panels, maximum power point trackers (MPPT) and invertor systems, and the one piece of advice I would always give is buy quality if you want it to work consistently well for a long period. Chinese manufactured goods just do not (yet) cut the mustard as a general rule. This one seems to be made in Canada (makes sense with their culture of the outdoors).

    http://www.selectsolar.co.uk/prod/299/eco-energy-dual-battery-solar-charge-regulator

    If you want to understand technically what is going on in the panels and regulators (MPPT), have a read of this. You will see that by tilting the panel 30 degrees towards the south will also give you 13% output for you panel.

    http://www02.abb.com/global/grabb/grabb101.nsf/0/4cfa9fa093ec55e8c12577a8002f7346/$file/10+tech+application+paper+n10+1sdc007109g0201.pdf

    Don’t forget that you need to fuse/circuit breaker all of this to prevent fires. The only problem is when you get a short circuit on a solar panel, you get about an extra 5% current flow (compared with a battery that will give up to 5000% extra flow). Fuses/circuit beakers that are designed to blow/trip under these circumstances are again expensive. They are however essential. The same rule as before: you get what you pay for. Do not expect a cheap device to achieve the same level of safety as an expensive one… here is how the assembly, test and calibration is done in the cheaper factories. I suspect this unit would not prevent a fire in any circumstance. http://youtu.be/NrplvHS2Uf8

    As far as cables go, you have 100W at 12v meaning that a 10A cable would suffice. Copper cable is copper cable at the end of the day, as in you local electrical wholesalers for some cable to handle 10A over a maximum run of 10m. I suspect that 2.5mm^2 could cover it, but check with the guy who knows in the specialist shop.

    Good luck and get some photos up once you have it running.

    Steve

    in reply to: Solar Panel Help #137242
    Ste_Mulv
    Participant

    REPLY Solar Panel Help
    Hi Chris,

    I just searched in google for “12v Solar Panel Regulators” and I quickly found this product which would more than suit your need and it also has isolated dual outputs so you can connected to you main and leisure batteries to keep them both topped up with out worrying about draining you main battery. I have a fairly good knowledge of solar panels, maximum power point trackers (MPPT) and invertor systems, and the one piece of advice I would always give is buy quality if you want it to work consistently well for a long period. Chinese manufactured goods just do not (yet) cut the mustard as a general rule. This one seems to be made in Canada (makes sense with their culture of the outdoors).

    http://www.selectsolar.co.uk/prod/299/eco-energy-dual-battery-solar-charge-regulator

    If you want to understand technically what is going on in the panels and regulators (MPPT), have a read of this. You will see that by tilting the panel 30 degrees towards the south will also give you 13% output for you panel.

    http://www02.abb.com/global/grabb/grabb101.nsf/0/4cfa9fa093ec55e8c12577a8002f7346/$file/10+tech+application+paper+n10+1sdc007109g0201.pdf

    Don’t forget that you need to fuse/circuit breaker all of this to prevent fires. The only problem is when you get a short circuit on a solar panel, you get about an extra 5% current flow (compared with a battery that will give up to 5000% extra flow). Fuses/circuit beakers that are designed to blow/trip under these circumstances are again expensive. They are however essential. The same rule as before: you get what you pay for. Do not expect a cheap device to achieve the same level of safety as an expensive one… here is how the assembly, test and calibration is done in the cheaper factories. I suspect this unit would not prevent a fire in any circumstance. http://youtu.be/NrplvHS2Uf8

    As far as cables go, you have 100W at 12v meaning that a 10A cable would suffice. Copper cable is copper cable at the end of the day, as in you local electrical wholesalers for some cable to handle 10A over a maximum run of 10m. I suspect that 2.5mm^2 could cover it, but check with the guy who knows in the specialist shop.

    Good luck and get some photos up once you have it running.

    Steve

    in reply to: Solar Panel Help #137231
    Ste_Mulv
    Participant

    REPLY Solar Panel Help
    Hi Chris,

    I just searched in google for “12v Solar Panel Regulators” and I quickly found this product which would more than suit your need and it also has isolated dual outputs so you can connected to you main and leisure batteries to keep them both topped up with out worrying about draining you main battery. I have a fairly good knowledge of solar panels, maximum power point trackers (MPPT) and invertor systems, and the one piece of advice I would always give is buy quality if you want it to work consistently well for a long period. Chinese manufactured goods just do not (yet) cut the mustard as a general rule. This one seems to be made in Canada (makes sense with their culture of the outdoors).

    http://www.selectsolar.co.uk/prod/299/eco-energy-dual-battery-solar-charge-regulator

    If you want to understand technically what is going on in the panels and regulators (MPPT), have a read of this. You will see that by tilting the panel 30 degrees towards the south will also give you 13% output for you panel.

    http://www02.abb.com/global/grabb/grabb101.nsf/0/4cfa9fa093ec55e8c12577a8002f7346/$file/10+tech+application+paper+n10+1sdc007109g0201.pdf

    Don’t forget that you need to fuse/circuit breaker all of this to prevent fires. The only problem is when you get a short circuit on a solar panel, you get about an extra 5% current flow (compared with a battery that will give up to 5000% extra flow). Fuses/circuit beakers that are designed to blow/trip under these circumstances are again expensive. They are however essential. The same rule as before: you get what you pay for. Do not expect a cheap device to achieve the same level of safety as an expensive one… here is how the assembly, test and calibration is done in the cheaper factories. I suspect this unit would not prevent a fire in any circumstance. http://youtu.be/NrplvHS2Uf8

    As far as cables go, you have 100W at 12v meaning that a 10A cable would suffice. Copper cable is copper cable at the end of the day, as in you local electrical wholesalers for some cable to handle 10A over a maximum run of 10m. I suspect that 2.5mm^2 could cover it, but check with the guy who knows in the specialist shop.

    Good luck and get some photos up once you have it running.

    Steve

    in reply to: Solar Panel Help #137227
    Ste_Mulv
    Participant

    REPLY Solar Panel Help
    Hi Chris,

    I just searched in google for “12v Solar Panel Regulators” and I quickly found this product which would more than suit your need and it also has isolated dual outputs so you can connected to you main and leisure batteries to keep them both topped up with out worrying about draining you main battery. I have a fairly good knowledge of solar panels, maximum power point trackers (MPPT) and invertor systems, and the one piece of advice I would always give is buy quality if you want it to work consistently well for a long period. Chinese manufactured goods just do not (yet) cut the mustard as a general rule. This one seems to be made in Canada (makes sense with their culture of the outdoors).

    http://www.selectsolar.co.uk/prod/299/eco-energy-dual-battery-solar-charge-regulator

    If you want to understand technically what is going on in the panels and regulators (MPPT), have a read of this. You will see that by tilting the panel 30 degrees towards the south will also give you 13% output for you panel.

    http://www02.abb.com/global/grabb/grabb101.nsf/0/4cfa9fa093ec55e8c12577a8002f7346/$file/10+tech+application+paper+n10+1sdc007109g0201.pdf

    Don’t forget that you need to fuse/circuit breaker all of this to prevent fires. The only problem is when you get a short circuit on a solar panel, you get about an extra 5% current flow (compared with a battery that will give up to 5000% extra flow). Fuses/circuit beakers that are designed to blow/trip under these circumstances are again expensive. They are however essential. The same rule as before: you get what you pay for. Do not expect a cheap device to achieve the same level of safety as an expensive one… here is how the assembly, test and calibration is done in the cheaper factories. I suspect this unit would not prevent a fire in any circumstance. http://youtu.be/NrplvHS2Uf8

    As far as cables go, you have 100W at 12v meaning that a 10A cable would suffice. Copper cable is copper cable at the end of the day, as in you local electrical wholesalers for some cable to handle 10A over a maximum run of 10m. I suspect that 2.5mm^2 could cover it, but check with the guy who knows in the specialist shop.

    Good luck and get some photos up once you have it running.

    Steve

    in reply to: Solar Panel Help #137223
    Ste_Mulv
    Participant

    REPLY Solar Panel Help
    Hi Chris,

    I just searched in google for “12v Solar Panel Regulators” and I quickly found this product which would more than suit your need and it also has isolated dual outputs so you can connected to you main and leisure batteries to keep them both topped up with out worrying about draining you main battery. I have a fairly good knowledge of solar panels, maximum power point trackers (MPPT) and invertor systems, and the one piece of advice I would always give is buy quality if you want it to work consistently well for a long period. Chinese manufactured goods just do not (yet) cut the mustard as a general rule. This one seems to be made in Canada (makes sense with their culture of the outdoors).

    http://www.selectsolar.co.uk/prod/299/eco-energy-dual-battery-solar-charge-regulator

    If you want to understand technically what is going on in the panels and regulators (MPPT), have a read of this. You will see that by tilting the panel 30 degrees towards the south will also give you 13% output for you panel.

    http://www02.abb.com/global/grabb/grabb101.nsf/0/4cfa9fa093ec55e8c12577a8002f7346/$file/10+tech+application+paper+n10+1sdc007109g0201.pdf

    Don’t forget that you need to fuse/circuit breaker all of this to prevent fires. The only problem is when you get a short circuit on a solar panel, you get about an extra 5% current flow (compared with a battery that will give up to 5000% extra flow). Fuses/circuit beakers that are designed to blow/trip under these circumstances are again expensive. They are however essential. The same rule as before: you get what you pay for. Do not expect a cheap device to achieve the same level of safety as an expensive one… here is how the assembly, test and calibration is done in the cheaper factories. I suspect this unit would not prevent a fire in any circumstance. http://youtu.be/NrplvHS2Uf8

    As far as cables go, you have 100W at 12v meaning that a 10A cable would suffice. Copper cable is copper cable at the end of the day, as in you local electrical wholesalers for some cable to handle 10A over a maximum run of 10m. I suspect that 2.5mm^2 could cover it, but check with the guy who knows in the specialist shop.

    Good luck and get some photos up once you have it running.

    Steve

    in reply to: Solar Panel Help #137239
    Ste_Mulv
    Participant

    REPLY Solar Panel Help
    Hi Chris,

    I just searched in google for “12v Solar Panel Regulators” and I quickly found this product which would more than suit your need and it also has isolated dual outputs so you can connected to you main and leisure batteries to keep them both topped up with out worrying about draining you main battery. I have a fairly good knowledge of solar panels, maximum power point trackers (MPPT) and invertor systems, and the one piece of advice I would always give is buy quality if you want it to work consistently well for a long period. Chinese manufactured goods just do not (yet) cut the mustard as a general rule. This one seems to be made in Canada (makes sense with their culture of the outdoors).

    http://www.selectsolar.co.uk/prod/299/eco-energy-dual-battery-solar-charge-regulator

    If you want to understand technically what is going on in the panels and regulators (MPPT), have a read of this. You will see that by tilting the panel 30 degrees towards the south will also give you 13% output for you panel.

    http://www02.abb.com/global/grabb/grabb101.nsf/0/4cfa9fa093ec55e8c12577a8002f7346/$file/10+tech+application+paper+n10+1sdc007109g0201.pdf

    Don’t forget that you need to fuse/circuit breaker all of this to prevent fires. The only problem is when you get a short circuit on a solar panel, you get about an extra 5% current flow (compared with a battery that will give up to 5000% extra flow). Fuses/circuit beakers that are designed to blow/trip under these circumstances are again expensive. They are however essential. The same rule as before: you get what you pay for. Do not expect a cheap device to achieve the same level of safety as an expensive one… here is how the assembly, test and calibration is done in the cheaper factories. I suspect this unit would not prevent a fire in any circumstance. http://youtu.be/NrplvHS2Uf8

    As far as cables go, you have 100W at 12v meaning that a 10A cable would suffice. Copper cable is copper cable at the end of the day, as in you local electrical wholesalers for some cable to handle 10A over a maximum run of 10m. I suspect that 2.5mm^2 could cover it, but check with the guy who knows in the specialist shop.

    Good luck and get some photos up once you have it running.

    Steve